Problem with GSDML file

Hello,
i'm trying to add the GSDML file v2.32 from plcnext axc f 2152 to the tia portal v13 in siemens.
My problem is that I can't add the GSDML file to tia portal because of an error it gives me, is there any way to fix this?

Comments

  • Hello,

    Can you please post the complete error message from TIA portal? (It is cut short in the screen shot).

    ~ Martin.

  • Hi, Martin, thanks for answering.

    This is the full error message:

    GSDML-V2.32-Phoenix+Contact+AXC+F+2152+-V1.0-20190923.xml
    :General GSD Error: Check-Number: 0x00020001,Message: The attribute MultipleWriteSupported must be set to 'true' if the attribute StartupMode contains the value 'Advanced'.,Line: 0,XPath: //DeviceAccessPointItem[@ID='DIM 1']/SystemDefinedSubmoduleList/InterfaceSubmoduleItem/ApplicationRelations/@StartupMode[.=';Legacy

  • Thanks for the additional info. We'll get back to you with an answer asap.

    ~ Martin.

  • Hello,

    I have an answer from our experts:

    Service Pack 1 of TIA 13 fixes a bug with GSDML imports, and once this Service Pack is installed the GSDML import should work.

    Here is an image showing the successful import of the GSDML file in TIA portal v13 SP1:

    8ABD9A16 5300 4A2D BACB 551EFB2F9590

     

    Hope this helps.

    ~ Martin.