AXC F 2152 with Siemens distributed IO station
Hello,
Is it possible to realize the following setup:
- AXC F 2152 with a safety extension AXC F XT SPLC1000
And connect this to a Siemens distributed IO station:
- IM 151-3 PN with regular IO and safety IO
Is this possible in the first place? And if so, is there any documentation on how to do this in PLCNext?
Upfront many thanks!
Comments
Here are some comments from our Safety experts:
The GSDML file for ET200S (GSDML-V2.25-Siemens-ET200S-20191007.xml) does not contain any PROFIsafe devices. Therefore these are not configurable in any controller via GSDML import. i.e. these only run on Siemens controllers where the catalog import is done via HSPs (HardwareSupportPackages).
If there was a GSDML file with safety modules, then you would still need a separate tool for the calculation of the iPar CRC (a checksum to secure the parameters). You would need to check with Siemens if they offer a tool to do this calculation.
Possible solutions:
- Get another GSDML from Siemens that includes PROFIsafe modules. Siemens will also need to provide a tool to calculate the iPar CRC.
- Install ET200SP instead of ET200S
- Instead of Siemens, use any other manufacturer (Phoenix INLINE / AXIOLINE / if necessary also WAGO / MURR / Bihl+Wiedemann / ....., which are designed to be compatible with controllers from other manufacturers).
Someone from your local Phoenix Contact office can get in touch with you to discuss this further, if you want.