PLCnext OPC UA ( SIM)
Trying to connect to OPC Ua on the SIM and I have managed to get UA Expert to connect, but when I try the same connection with Cogent Data Hub I get an error ;
"BadIdentityTokenInvalid: The user identity token is not valid. Possible cause, the user token policy is not supported on the server."
I have the Authentication sent to User Name and am using admin and plcnext I have the endpoint URL set to opc.tcp://localhost:4840
Comments
If you do try other servers, then please note that installing multiple OPC UA servers on one PC - including the one in the PLCnext Engineer simulation - may cause conflicts on port 4840, so you should only have one OPC UA server running at once.
When using the Sim how do you get to the WBM
https :// localhost/WBM
https :// 192.168.1.30/WBM
https :// 10.0.2.15/WBM
All of above end up in a timeout webpage.
From the Info Center:
... so the WBM should be accessible on https://localhost:5050
ok thanks got into wbm