Firmware update from version 2021.0.3 LTS to 2023.0.0 LTS

I want use Codesys v3.5 runtime on my PLCnext controller but

i can't update firmware from 2021.0.3 LTS to 2023.0.0 LTS via WBM

firmware is allways unchanged stays on 2021.0.3 LTS version after reboot.

Where is the problem?

Comments

  • Dear Ivan,

    you have to Upgrade to 2022.x.x Firmware First. A direct Update from 2021 to 2023 ist Not possible

  • No. Thanks for info!

  • edited April 2023

    I try to update to 2022.0.8 LTS but it failed?

    Firmware is still old one 2021.0.3 LTS

  • Can you confirm that you are using the procedure described on this page to upgrade the firmware to version 2022.0.8 LTS?

    If that does not work, please try this procedure:

    • Copy the .rauc file for firmware version 2022.0.8 to the opt/plcnext directory on the controller (e.g. using WinSCP or just scp on a Windows command line) .
    • Start an SSH connection (e.g. with Putty or just ssh on a Windows command line) and enter the following command: sudo update-axcf2152

    Please take note of any error messages that appear.

    If the procedure is successful the controller should reboot and the new firmware version should be installed.

  • Thanks for answer. I didn't manage to update firmware to newer version throught WBM but suddenly I don't know

    how I manage to install Codesys Run time on PLCnext cotroller without error: update your firmware.