Good morning I would like to know if it was possible to change the DNS name or as for siemens create an OPC interface to assign the name you want, eg PLC_TEST

Thanks in advance Greetings


Comments

  • Yes, you can change the DNS name in the field shown in your screen shot. That particular field will only change the DNS name in the self-signed OPC UA Server Certificate that is generated automatically.

    The client can access the OPC UA server on the PLC using a DNS name. In your application, how will the client be resolving DNS names to IP addresses?

  • Hi, thank you very much.. In fact I was wrong to enter the capital letter XD