Skip to content

Creating image file from AXC F 2152 and AXC F XT SPLC 1000

Hello All,

I am using the following hardware :

1) AXC F 2152

2) AXC F XT SPLC 1000 

3) AXL F PSDI8/4 1F

4) AXL F DI8/1 DO8/1 1H

The project is finished and runs on an SD card with part number 1043501. Now I want to distribute the software without sending the source code. Instead, I like to make a binary file or image file from an SD card and shipped to the customer. I want to know if it is possible to read the SD card and make an image file for both safety and non-safety SW. Later, on the customer side only by inserting the SD card on AXC F 2152 system will boot up.

Thank you very much in advance!

Ayoub

Comments

  • I got help from Phoenix in Sweden (especially thanks to Johan : ) for his great help) and the following solution worked for me. With this solution, you can make backups for both the safe and non-safe SWs, HMI, and even users.

    First Download the project on the HWs and then execute the following commands:


  • There is new pc app at the store, wich create application from downloaded to plc project. It can be sutable in some cases. Please take alook at https://www.plcnextstore.com/world/app/2213

    Best regards

Sign In or Register to comment.