Codesys Control for PLCnext SL
Good day
Regarding Codesys Control for PLCnext SL
Devices used:
AXC F 2152
Software used:
Codesys V3.15 SP19 Patch 4
I have configured the IP and installed the Update PLCnext tool via the Codesys platform. The PLC can be pinged and connected via PLCnext from the Codesys Platform.
My Issue is that I can not connect or see the device when I scan for network devices.
Any info will be highly appreciated.
Comments
This sounds like a problem with either the Codesys runtime or the Codesys IDE, or both.
If no one in the PLCnext Community can help, then the best bet is probably to contact Codesys support.
Good day Martin
I finally found the issue and would like to share my results.
Process:
If you use the PLCnext Engineer (Phoenix IDE) it would read the Local Bus 100%.
But if you are using Codesys Control for PLCnext there are some Modules that it can not identify.
I bult the Local Bus as follows, NOTE that this configuration was built by Project+ "Phoenix Software Tool".
This layout DID NOT work because of the Local Buss Not Running Error
Slot 1: AXL SE DO16/1 - Digital module
Slot 2: AXL SE DI16/1 - Digital module
Slot 3: AXL SE PD16 24V - Potential distributors
Slot 4: AXL SE PD16 GND - Potential distributors
Slot 5: AXL SE SC-A - Cover
Slot 6: AXL SE SC-A - Cover
After I decided to change the Local Bus to the following configuration, The PLC and Local Bus was HAPPY and worked successfully.
Slot 1: AXL SE DO16/1 - Digital module
Slot 2: AXL SE DI16/1 - Digital module
Slot 3: AXL SE SC-A - Cover
Slot 4: AXL SE SC-A - Cover
Slot 5: AXL SE SC-A - Cover
Slot 6: AXL SE SC-A - Cover
Result:
Codesys or Codesys Control for PLCnext, has a PROBLEM to identify the following Modules.
AXL SE PD16 24V - Potential distributors
AXL SE PD16 GND - Potential distributors
Thank you for the update.
The support for I/O modules by the Codesys IDE and runtime is entirely outside our control, so I am afraid that you will need to contact Codesys about this problem. In any case, this information will be very helpful for other users of the Codesys runtime who might experience a similar problem.