IEC 60870-5-104 IN SMART RTU
Dear Expert
I'm using SMART RTU with diagram below.
The connection Downlink and Uplink was OK.
But when I configure double command signal, I didn't see " Select before execute" field of SendList table. So I couldn't use doube command with Select before Execute.
How can I fix it?
Many Thank.
Comments
Hello John_Capture,
the parameter you are looking for can be found in the "Project work / I/O-Parameter setting / Double command output" area
The selection can be made here for each double command.
Best regards
Dear Sir
Thank for your feedback.
I think that this window was only for binary output module, in my diagram is protocol converter. It mean that this tab can't apply for my diagram.
Is this true or no?
on other hand, I tried with Double command DO to SBO function. But it didn't work.
Bests
Dear Sir.
Do you have any solution
Best
Hello,
you are right the current feedback configurate via the I/O parameter path is for binary outputs or for conversion into a corresponding message/double-point information.
After re-analyzing your request and since it is a direct pass-through UL 104 - DL 104 (without handling in the application), the selection mechanism "Selection before execute" should be passed through 1:1 and no further activation is therefore necessary.
Dear Sir
Thank for your feedback.
Best and Regard.
Dear Thomas.
I guess that the problem happen at IEC60870-5-104 Downlink in Smart RTU.
because I tried test with other case as below picture and it can't still work
May SBO in IEC60870-5-104 in Downlink connection have problem.