Firmware update from 1.0.0.250
Hello,
i have a very old AXL F 2152, HW2 FW 1.0.0.250. The webpage does not provide any options to update the firmware. What tools or instructions does PxC provide to be able to update the unit firmware.
Hello,
i have a very old AXL F 2152, HW2 FW 1.0.0.250. The webpage does not provide any options to update the firmware. What tools or instructions does PxC provide to be able to update the unit firmware.
Comments
Hi Gmathisz,
In early firmware's like that, updates must be done via the command line. You can use protocols like FTP to move the .raucb update file to the controller and SSH to remote into the command line.
People often use WinSCP for FTP and Putty for SSH, but my favorite tool is MobaXterm which can do both.
Once you FTP the update file onto the controller you must create a root user then issue the update command with:
'sudo update-axcf2152'
Here is some information about connecting to the controller via SSH and using FTP:Connecting to the controller
With the above instructions i managed to update to the controller to 2024.0.8 LTS. A couple of notes in case it might help somebody in the same situation:
That's good to know. Anyone that needs to do something similar can also refer to the process described in the PLCnext Technology Info Center, which is similar to what you have described: