Hi,

I downloaded https://www.plcnextstore.com/#/192 and tried to use the block PNFD_IL_DIAG and in manual it refers to AsynCom_PN_Info_V1_01.

I can't find that block in the folders. I have downloaded the asyncom library but it is not in that library as well. 

 

Best regards Stefan

Comments

  • This is a documentation error. AsynCom_PN_Info* does only exist in PC Worx 6, not in PLCnext Engineer.

  • Should I use some other block to read all profinet devices or is it not possible to use PNFD_IL_DIAG  in plcnext?

    Br Stefan

  • It is possible to use PNFD_IL_DIAG like this:

     

    8 PNFD_IL_Diag

    ...

    Then we have to fill out the FDestAddr and the SlotID for the safety module. Here we have the safety module on
    slot 3 at the first bus coupler and on slot 1 at the second bus coupler. The first safety module has the FDestAddr
    33 with the NodeID 90 and the second FDestAddr 35 with NodeID 112.

     

    In PC Worx 6 this is done by AsynCom_PN_Info. But this is technically not possible in PLCnext.

    That AsynCom_PN_Info was mentioned in the PLCnext documentation was a mistake because the PLCnext documentation was created from the PC Worx 6 documentation.

    Best regards, Oliver

  • Ok. then it should be possible to read diagnostic to PLC software.

    What about the data type ASYN_ARR_DEVICES_PN_0_255, I get error is inaccessible on that data type.

    /Stefan

     

  • ASYN_ARR_DEVICES_PN_0_255 is provided by the AsynCom library and used in PN_Dev_Diag.

    If you include PN_Dev_Diag_4 in your PLCnext project it should work.

    If you want to use ASYN_ARR_DEVICES_PN_0_255 directly in your PLCnext project you have to include AsynCom_9 in your PLCnext project too.

    AsynCom_9.pcwlx is includes in the MSI file (https://www.plcnextstore.com/#/192, PLCNE_PN_Dev_Diag_4_20200305.msi) too.

    If there are any more problems please send your PLCnext project to automation-service@phoenixcontact.com with the call number 00128406 in the subject of your email.

    Thank you and kind regards, Oliver