D-LED flashing on a Starter Kit

edited April 2020 in PLCnext Engineer

Hi,

On my PLCNext starter kit running on "HW: 02 FW: 2020.0.1 LTS" my D LED is flashing red so something is wrong with the Bus.

I created a new project added the "AXL F DI8/1 DO8/1 1H" and the "AXL F AI2 AO2 1H Rev. >= 02/1.00" and uploaded this config to the PLC.

On the IO cards the D LED is off, only the UA is green.

Then the D LED flashes red so something is wrong.

 

Below is my Output.log file can some one tell me what is wrong or did I get an DOA?

 

18.03.20 19:59:17.947 CommonRemoting                                               INFO  - Accepted connection #0: connectionId=0081C560, 192.168.1.20 -> 0.0.0.0:4110018.03.20 19:59:17.947 CommonRemoting                                               INFO  - Accepted connection #0: connectionId=0081C560, 192.168.1.20 -> 0.0.0.0:4110018.03.20 19:59:22.970 CommonRemoting                                               INFO  - Connection was lost remotely, connectionId=0081C56018.03.20 19:59:22.975 CommonRemoting                                               INFO  - Closing connection: connectionId=0081C56018.03.20 19:59:31.211 CommonRemoting                                               INFO  - Accepted connection #0: connectionId=00818860, 192.168.1.20 -> 0.0.0.0:4110018.03.20 19:59:38.646 Arp.System.Security.Services.PasswordAuthenticationServiceImpl INFO  - Successful authentication for name="admin": connectionId=00818860, securityToken=F5EF01DA18.03.20 20:00:32.308 Arp.Services.ProfiCloud.Internal.ProficloudTSDAdapter        INFO  - Stopped Proficloud TSD service18.03.20 20:00:32.309 Arp.Services.ProfiCloud.Internal.ProficloudAppAdapter        INFO  - Stopped Proficloud AppStore service18.03.20 20:00:32.309 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 EhmiComponent: OnPlcStopping18.03.20 20:00:32.341 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Enter  StopPlc18.03.20 20:00:32.341 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 OnPlcStopped 18.03.20 20:00:32.343 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 ESDK 0xffff, SetRunMode, run=018.03.20 20:00:32.343 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Exit   StopPlc. Elapsed=218.03.20 20:00:32.345 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 Enter EhmiComponent: OnPlcStopped18.03.20 20:00:32.346 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680    Cannot find authorizationTokenTimeout in project.json18.03.20 20:00:32.346 Arp.Services.Ehmi.EhmiComponent                              WARN  - 2697855680   LoadDefaultTimeout Cannot get sessionTimeout from project.json18.03.20 20:00:32.347 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 Exit  EhmiComponent: OnPlcStopped18.03.20 20:00:32.675 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 Enter EhmiComponent: OnPlcUnloading, onError=false18.03.20 20:00:33.505 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680   Clear 18.03.20 20:00:33.505 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 Exit  EhmiComponent: OnPlcUnloading18.03.20 20:00:33.545 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Enter  ResetPlc. isChanging=false18.03.20 20:00:33.545 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 OnPlcUnloaded PlcLoaded=true18.03.20 20:00:33.546 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 ESDK 0xffff, Enter RemoveAllAssemblies18.03.20 20:00:33.546 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 ESDK 0xffff, Exit  RemoveAllAssemblies18.03.20 20:00:33.546 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Exit   ResetPlc. Elapsed=118.03.20 20:00:33.551 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Enter  UnloadPlc. isChanging=false18.03.20 20:00:33.551 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 OnPlcUnloaded PlcLoaded=false18.03.20 20:00:33.552 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Exit   UnloadPlc. Elapsed=018.03.20 20:00:34.010 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 EhmiComponent: OnPlcUnloaded, onError=false18.03.20 20:00:39.684 Arp.Services.ProfiCloud.Internal.ProficloudTSDAdapter        INFO  - Could not read GDS metrics file /opt/plcnext/projects/ProfiCloud/metrics.json.18.03.20 20:00:39.685 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 EhmiComponent: OnPlcLoading18.03.20 20:00:40.417 Arp.Plc.Esm.Internal.TaskController                          INFO  - Configuring Sleep class with a sync point interval of 100000us, an watchdog interval of 100000us and an axio interval of 100000us18.03.20 20:00:41.534 Arp.Io.Axioline.Internal.AxiolineDomain                      INFO  - Axioline: Load tic configuration.18.03.20 20:00:41.536 Arp.Io.Axioline.Internal.AxiolineDomain                      INFO  - Axioline: XML-File: 1.tic18.03.20 20:00:41.541 Arp.Io.Axioline.Internal.AxiolineDomain                      INFO  - Axioline: XML-File: 2.tic18.03.20 20:00:41.547 Arp.Io.Axioline.Internal.AxiolineDomain                      INFO  - Axioline: XML-File: edd5192e-ba64-49c7-b0c8-76f62f3d6e38.tic18.03.20 20:00:41.554 Arp.Io.Axioline.Internal.TicConfig.Tic2ConfigSvc             INFO  - Axioline: Start converting tic files.18.03.20 20:00:41.555 Arp.Io.Axioline.Internal.System                              INFO  - Axioline: Initialize/configure bus.18.03.20 20:00:41.632 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: Bus confirmation with negative result (command 0x8711, errCode 0xa2f, addInfo 0x0). Continue download.18.03.20 20:00:41.635 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: Bus confirmation with negative result (command 0x8728, errCode 0xa02, addInfo 0x4). Continue download.18.03.20 20:00:41.638 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: PDI confirmation with negative result (Command 0x8042, slot 0x1, index 0x14, errCode 0xf22, addInfo 0x1). Continue download.18.03.20 20:00:41.640 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: PDI confirmation with negative result (Command 0x8042, slot 0x1, index 0x15, errCode 0xf22, addInfo 0x1). Continue download.18.03.20 20:00:41.643 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: PDI confirmation with negative result (Command 0x8042, slot 0x1, index 0xff8d, errCode 0xf22, addInfo 0x1). Continue download.18.03.20 20:00:41.646 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: PDI confirmation with negative result (Command 0x8042, slot 0x1, index 0xff8f, errCode 0xf22, addInfo 0x1). Continue download.18.03.20 20:00:41.649 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: PDI confirmation with negative result (Command 0x8042, slot 0x2, index 0x14, errCode 0xf22, addInfo 0x2). Continue download.18.03.20 20:00:41.652 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: PDI confirmation with negative result (Command 0x8042, slot 0x2, index 0x15, errCode 0xf22, addInfo 0x2). Continue download.18.03.20 20:00:41.655 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: PDI confirmation with negative result (Command 0x8042, slot 0x2, index 0x24, errCode 0xf22, addInfo 0x2). Continue download.18.03.20 20:00:41.657 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: PDI confirmation with negative result (Command 0x8042, slot 0x2, index 0x29, errCode 0xf22, addInfo 0x2). Continue download.18.03.20 20:00:41.660 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: PDI confirmation with negative result (Command 0x8042, slot 0x2, index 0x29, errCode 0xf22, addInfo 0x2). Continue download.18.03.20 20:00:41.663 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: PDI confirmation with negative result (Command 0x8042, slot 0x2, index 0x2f, errCode 0xf22, addInfo 0x2). Continue download.18.03.20 20:00:41.665 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: PDI confirmation with negative result (Command 0x8042, slot 0x2, index 0x80, errCode 0xf22, addInfo 0x2). Continue download.18.03.20 20:00:41.669 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: Bus confirmation with negative result (command 0x8714, errCode 0xa02, addInfo 0x4). Continue download.18.03.20 20:00:41.673 Arp.Io.Axioline.Internal.AxioMxi                             WARN  - Axioline: Bus confirmation with negative result (command 0x8701, errCode 0xa02, addInfo 0x4). Continue download.18.03.20 20:00:41.674 Arp.Io.Axioline.Internal.System                              INFO  - Axioline: Connect to shared FbIo System.18.03.20 20:00:41.674 Arp.Io.Axioline.Internal.System                              INFO  - sleep mode18.03.20 20:00:41.678 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Enter  LoadPlc. isChanging=false18.03.20 20:00:41.689 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Exit   LoadPlc. Elapsed=1018.03.20 20:00:41.695 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Enter  SetupPlc. isChanging=false, startKind=Warm18.03.20 20:00:41.696 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 OnPlcLoaded PlcLoaded=false18.03.20 20:00:41.696 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 ESDK 0xffff, AddAssemblies, toInstanceID=110, toSize=256, otInstanceID=100, otSize=25618.03.20 20:00:41.696 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 LogStatistics cycle=26/27, active=0/2, esdk=0/2, gds=0/118.03.20 20:00:41.697 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Exit   SetupPlc. Elapsed=318.03.20 20:00:41.799 Arp.Plc.Gds.Internal.GdsDomain                               INFO  - GDS configuration successfully loaded.18.03.20 20:00:41.880 Arp.Plc.Gds.Internal.GdsDomain                               INFO  - GDS data connections successfully created.18.03.20 20:00:41.884 Arp.Plc.Gds.Internal.Subscription.SubscriptionBase           WARN  - Nothing to subscribe for ID 10! Please add some variables...18.03.20 20:00:42.064 Arp.Plc.Gds.Internal.Subscription.SubscriptionBase           WARN  - Nothing to subscribe for ID 10! Please add some variables...18.03.20 20:00:42.067 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 Enter EhmiComponent: OnPlcLoaded18.03.20 20:00:42.068 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680    Cannot find authorizationTokenTimeout in project.json18.03.20 20:00:42.069 Arp.Services.Ehmi.EhmiComponent                              WARN  - 2697855680   LoadDefaultTimeout Cannot get sessionTimeout from project.json18.03.20 20:00:42.070 Arp.Services.Ehmi.EhmiComponent                              WARN  - 2697855680   ReadChecksumFromFile Cannot ReadChecksumFromFile18.03.20 20:00:42.071 Arp.Services.Ehmi.EhmiComponent                              WARN  - 2697855680    Cannot read the type.dictionary.json file.18.03.20 20:00:42.071 Arp.Services.Ehmi.EhmiComponent                              WARN  - 2697855680    TypeDictionary->Load() failure!!!18.03.20 20:00:42.073 Arp.Services.Ehmi.EhmiComponent                              WARN  - 2697855680   ReadProjectChecksumFromFile Cannot GetFileChecksum18.03.20 20:00:42.074 Arp.Services.Ehmi.EhmiComponent                              WARN  - 2697855680   Load Cannot read fileName=data.dictionary.json18.03.20 20:00:42.074 Arp.Services.Ehmi.EhmiComponent                              WARN  - 2697855680    DataDictionary->Load() failure!!!18.03.20 20:00:42.075 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 Exit  EhmiComponent: OnPlcLoaded18.03.20 20:00:44.631 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 EhmiComponent: OnPlcStarting, startKind=Warm18.03.20 20:00:44.634 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Enter  StartPlc. startKind=Warm18.03.20 20:00:44.634 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 OnPlcStarted 18.03.20 20:00:44.634 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 ESDK 0xffff, SetRunMode, run=118.03.20 20:00:44.634 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 LogStatistics cycle=25/26, active=0/1, esdk=0/1, gds=0/118.03.20 20:00:44.634 Arp.Io.EthernetIP.EthernetIPComponent                        INFO  - 2973758144 Exit   StartPlc. Elapsed=118.03.20 20:00:44.652 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 Enter EhmiComponent: OnPlcStarted18.03.20 20:00:44.653 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680    Cannot find authorizationTokenTimeout in project.json18.03.20 20:00:44.654 Arp.Services.Ehmi.EhmiComponent                              WARN  - 2697855680   LoadDefaultTimeout Cannot get sessionTimeout from project.json18.03.20 20:00:44.655 Arp.Services.Ehmi.EhmiComponent                              INFO  - 2697855680 Exit  EhmiComponent: OnPlcStarted

Comments

  • Hello,
    this looks like something is wrong with the configuration.

    Please have a look at the Web Based Management of your PLC for detailed diagnostic information.
    "ip.x.x.x/wbm" -> Diagnostics -> Localbus

    Or check out the Axioline Diagnose Registers in your Global Variables with the PLCnext Engineer Debug mode.
    kind regards,
    Oliver

  • Kick, hi Oliver our anybody else from the support team any suggestions what to try/do next.

     

  • Hey,
    the 0x0a2F looks like no Device is connected.
    please check the powersupply and the mounting of your IO devices.
    you can remove them and mount them again. 
    Make sure all the pins are straight  and the device is mounted tightly.

    What happens if you download another configuration?

    This could either be caused by a wrong Config file (TIC file) or that the devices are not properly connected.
    kind regards,
    Oliver

  • Pulled AXC 2151, the input card 2701916, the anolog input 2702072 from the staterkit board.

    All the pins are straight and not bent.

    What do you mean with "What happens if you download another configuration?" I only have the digital and analog card in the starter kit.

    Bare in mind  I am a newbie just starting with the startkit.

    I created a new project added the "AXL F DI8/1 DO8/1 1H" and the "AXL F AI2 AO2 1H Rev. >= 02/1.00" and uploaded this config to the PLC.

    I followed this youtube guy

     

     

  • Hi plcnext911,

    hmm, sounds all a bit strange.

    Maybe it would be the best to have a quuck remote session to help you out.

    I'll come back to you by mail.

    Take care

    Frank

  • a pin on the bus connector was bent and caused the error message?

    Annotation 2020 04 24 110609

    The connector is realy fragile the same on the IO modules and one pin bending could happen a lot I think.

    Some quality testing before shipping out the Startkit could also be done I think.

  • Hello,
    sorry for this.
    If assembled correctly this should not happen.
    Mount the adapter on the DIN Rail and push it together.

    That way this can not happen...

    We are going to check the shipping and test protocols.
    Please send the StarterKit back to us through your local sales subsidiary for replacement.

    kind regards,

    Oliver.