Hello,

I built the sample program to test the connection of my PLC to the proficloud, but when i try to read them or locate them on the proficloud page it starts an infinite cycle saying "turn on your appliance".

I´ve been folloing the above tutorial and i get stuck around minute 2:23.

Been trying all sorts of tutorials or videos for the last couple weeks or so and i feel that i hit a wall, if someone can guide me i would apreciate 

Thank you in advance

 

 

Comments

  • Looks like that video skips the step where you setup the internet connection of the PLCnext. Make sure PLCnext has an active internet connection and you should be good.

  • Hi,

    It looks like the device can not reach the profilcoud. Did you check the Gateway-Address? Is the RTC set to UTC?