EPC1522 Profinet not working
I have an EPC1522 and created a project with PLCnext Engineer. I have an AXL F BK PN in my network. I can integrate and configure the BK with PLCnext Engineer but after downloading the project to the EPC, the Profinet diagnosis shows that the Profinet communication is lost. The same happens with a Profinet switch. What am I missing? Sending a ping to the BK works.
Comments