Dear PLCnext-Team,
I’m testing out the Starterkit 1188165 and have a Local bus error. Like in this discussion (https://www.plcnext-community.net/forum/#/discussion/1632/failed-to-list-local-bus-modules-on-webpage-when-running-starterkit-example), software installation, firmware update, connection with 2152 controller — everything is okay. But I have no interaction between controller and I/O modules. After that I found on WBM the local bus error.
I tried to isolate the problem and removed all modules with exception of AXL SE DO16/1 Rev. >=00/1.00. This module is placed in the first slot of the Module carrier AXL F BP SE4 (left above). In PLCnext Engineer I left also only the AXL SE DO16/1 Rev. >=00/1.00 in „Axioline F“.
But even this one modul isn’t been detected. Diagnostic Registers are:
- Diagnostic Status Register 0x0084
- Diagnostic Parameter Register 1 0x0c02
- Diagnostic Parameter Register 2 0x0002
Can you please help me find the source of the problem?
Best regards
Ivan