AXC 2152 With 12 Nos of ILC 131 Over Profinet Communication Issue

Hello, I am Using AXC 2152 With Total 12 Nos ILC 131 ETH. I have established Communication over Profinet , Communication having Conitous Warning (0x0020(Neighborhood devices information is not available)) , due to which DATA Update Rate is very Poor. Can we establis Stable and Good Communication with this configuration?

Hello Harshid, please add a Output.log for diagnostic details. The missing Neighborhood information is most likely unrelated to the communication delay. This just means that there is a Device that does not support neighborhood information… how high is the load of your Application? maybe the PLC is overloaded? What is the Update Time of your PN Devices? Maybe you can reduce these…