Hello guys, I’m trying to connect AXC F 2152(controller) with Siemens S7 300 as a device via Profinet. I created the GSDML file, uploaded into PlcNext Engineer. Added and assigned this profinet module from s7 300 in my project. I’ve got this warning presented in uploaded image and data is not being sent. Do you know maybe where the problem lies? Thanks for any help Mateusz
Hi emasall, Bit 0 indicates that the PN device or the network does not support LLDP (neighbourhood detection), means the controller can not assign a PN name automatically in case the PN device is replaced.
However, this is not critical. More interesting is that the connection were lost, or better I assume that the device were never properly initiated. Can you attach to this post maybe the output.log file? You’ll find the log in /opt/logs/ and you can download the file via WinSCP… cu
Frank BTW: You can find the meaning of the statusbits in our PLCnext Info Center.
Dear Frank, thanks for your answer. I’m attaching file you’ve asked. Mateusz //Solved problem. It was problem with block in Tia Portal.