Axc_f_2152 firmware

I’m trying to download the AXC_F_2152 Firmware per the instructions into the my new AXC_F_2152 PLCNEXT. However, the zipped file did not produce a .*raucb file; see attached picture. Am I looking at the correct instructions? See attached picture. Can the firmware not be loaded via the SD card like the AXC _Sample PLCNEXT ?

Hello, I notice that there is an AXC_F _2152 Folder.

Is there no *.raucb inside the folder also?

I guess you “extracted to folder” instead of “extract here”.

Hi phinkel, A small addition to my colleague’s remark: The zip-file contains a .exe file. This is an self-extracting file and needs to be executed on the you WINDOWS-PC, and be ‘installed’. This file will extract the RACU file, mentioned in the update-manual, in the directory, chosen during it’s installation. When this is done, you can proceed with the update-process as listed.

Guess the manual needs to be tuned a bit to elaborate on this intermediate step.