AXC F3152 Profinet Port Gateway Settings

Hello,
I am using the AXCF3152 device. When configuring the network settings of the device through the web interface and entering the IP for X1, X2, X3 ports, when I input the Gateway for X2 (Profinet Port) and click apply, the device cannot see this gateway in its status. When we cut off the power and turn it back on, the device sets the Gateway to 0.0.0.0. What is the reason for this, and how can we resolve it?
WhatsApp Image 2023-12-21 at 14.55.40.jpeg
We want to set the gateway address as shown in the photo to 10.164.32.1, but it is not visible in the status.
Wishing you a happy new year.

Hello eren1010,
Normally on the Linux OS only one Gateway will be used. If the configured standart-gateway e.g. for „lan1“ on AXCF3152 will be found, then the configured gateways for „lan2“ and „lan3“ will be ignored (in WBM you will see 0.0.0.0).
Please find a similar question in this conversation:
Forum - PLCnext Community PLCnext Technology from Phoenix Contact is a unique, open ecosystem for modern automation that is capable of meeting all the challenges of the IoT world. BR Eduard