AXIO0016 error while importing IODD file

Hi all,
While trying to load the IODD template from my I/O module AL2301 from IFM to the phoenix contact AXL F IOL8 2H, the import succeed however I get the following error code:
AXIO0016 The AXL-F Submodule [4 : AL2301 Cyclic] overflows process data by 208 bits.
How could I solve this issue?

Module AL2301: https://www.ifm.com/fr/en/product/AL2301IODD src: https://www.ifm.com/download/files/IODD_AL2X01-Cyclic_IO-Link-11/$file/IODD_AL2X01-Cyclic_IO-Link-11.zip
Parameters of port 4:
AXIO0016 error.jpg

Hello.
This limitation is due to the max process datas length capacity of the IOL 8 : 64 bytes IN, and 64 bytes Out.
The AL2301 occupies 30 bytes (I + O), and so, the 64 bytes capacity is reached (with the other devices present in your configuration).

The workaround would be to use several IOL8 masters, and split several AL2301 on them
IOL8.png
You can contact Phoenix contact France : 33 1 60 17 98 98 for more details.

Hi
Thanks for your answer and the work around
Regards
Clement