Can I use AXF I/O modules together with AXC F IL ADAPT

Hi, I have question I need to use AXC F IL ADAPT, but after reading datasheet I think it’s not possible to use AXC I/O modules together with adapter but only IB modules, can someone confirm it?

That’s correct, the right side can only operate as an InLine local bus (with the InLine adapter) or as an Axioline bus. This selection must be made in PLCnext Engineer. It’s not possible to have both, e.g some Axioline modules followed by an InLine adapter.
You could put the InLine modules on a Profinet bus coupler, with the AXC F x152 as the Profinet controller.