Cannot online debug on PLCNext Engineer
Capture2 also I download project to device already. But can’t debug like other .
Capture 2019
Hello, I can reproduce this, but only if the online and offline projects do not match. Are you 100% sure that you were able to download the project to the PLC successfully? What version of PLCnext Engineer you are using, and what PLC firmware version? I see that the FAIL LED is lit. I am guessing that the RUN LED is flashing, so this indicates that the PLC program has stopped. If you are trying to diagnose the reason for this, then you can check the file /opt/plcnext/logs/Output.log, where you may see an entry like this: 12.07.19 01:22:08.929 Arp.Plc.Esm.Internal.TaskScheduler ERROR - Watchdog of task 'Cyclic100' triggered. (watchdog time 100000us / time after task start 100454us) (I have also moved this post to the PLCnext Engineer category).