Hello. I am new to PLC. I have AXC F 2152 controller. I want to connect my controller with MATLAB/Simulink software. How to establish profinet communication between them? Kindly can anyone guide me on this?

Hello. I am new to PLC. I have AXC F 2152 controller. I want to connect my controller with MATLAB/Simulink software. How to establish profinet communication between them? Kindly can anyone guide me on this?

If you want to establish Profinet communication, then I assume that the Matlab/Simulink software has Profinet communication capability - is that correct?
If so, does the device running the Matlab/Simulink software act as a Profinet controller or a Profinet device?
If it’s a Profinet device, do you have a GSDML file for the device?
If it’s a Profinet controller, you should be able to import the GSDML file for the AXC F 2152 into the Matlab/Simulink IDE. The GSDML file for the AXC F 2152 can be downloaded from the website, here:
https://www.phoenixcontact.com/en-pc/products/controller-axc-f-2152-2404267#downloads-link-target
Hello Martin, I am gonna run my simulink model on a raspberry pi model 4. So is it possible to communicate raspberry pi with 2152 PLC?
Hello.
The answer is the same regardless of what device the Simulink model is running on.
What communication interfaces does Simulink provide for communicating with partner devices? Profinet? OPC UA? Modbus/TCP? If Simulink provides a suitable communication interface, then it should be possible for the model to communicate with an AXC F 2152.
Have you considered running the Simulink model directly on the AXC F 2152?