I have a 24Vcc encoder , conected to a module AXL F CNT2 INC2 1F. I cant see any count or change on the data list of the module. whem the enconder move the lights of the module still off . I conect the channel A, B and Z and use the 24Vcc source from CN1. If I use the encoder in the counter module its work .
is necessary to active some input or byte to active the module?
Thanks

Hello Diego,
Please try the following settings:
Modulo = 1000dec
1LimitValOut = 0dec
2LimitValOut = 100dec
LimitValOut must not be equal to or greater than modulo.