Error Loading Balluff IO Link GSDML File

Hello, I’m having issues trying to load a GSDML file from a Balluff IO Link Master (BNI005H - BNI PNT-508-105-Z015). After importing the file through PLCnext Engineer, I get the following error message: “Import failed : The imported safety parameters are not valid. C:\\Users\\myUser\\Desktop\\Balluff Order\\BNI005H - BNI PNT-508-105-Z015\\ST_GSDML_BNI_PNT_508_105_Z015_DRF_894200_07_000\\GSDML-V2.34-Balluff-BNI-PNT-508-105-Z015-20190301.xml” Here is the link to the IO Link Master and you can find the link to download the GSDML file in the downloads section at the bottom: https://www.balluff.com/local/ca/productfinder/product/?key=BNI005H#/ Cheers, Phil

Phil, I tried using a BNI004U and had the same issue. What I did was open the GSDML file and search for “safety parameter”. Below that line is a small section starting and ending with F_ParameterRecordDataItem… Comment/delete that block and the GSDML should import. I just tested the import with 2019.9 and 2020.0 and they both looked good. Rob

Hi Rob, Thanks for the quick reply. Commenting out that block has solved the issue, thank you! ** will this have an effect on the safety parameters? Regards, Phil