GW PL ETH UNI-BUS with AXC F 2152
I’ve been working on building a Profinet demonstration board. I am having trouble connecting a GW PL ETH UNIT-BUS (P/N 2702233) to the Profinet structure. I have created a GSDML file with the devices connected to the GW and successfully imported it to the PLCNext Engineer project. I can set all the parameters but when I attempt to load the project to the controller, I get the BF-C Error LED and SF Error LED. My question is, has anyone successfully connected this device to the AXC F 2152 and was able to read data via Profinet or is this even possible? Configuration: PLCnext Engineer Version 2019.6 Controller: AXC F 2152 (FW 2019.6) | IP Address 192.168.1.2 GW PL ETH UNI-BUS(FW 2.20) w/ HART 4-BUS; GW PL HART8+AI-BUS (Temp sensor connected to HART8 module) | IP Address of Gateway 192.168.1.4 All devices have same Subnet Mask and Default Gateway.
PCWE_EX_CPP_LibmodbusTCP_2.zip
EX_CPP_LibmodbusTCP_2.PDF
Wireshark Capture (Cannot upload GSDML file due to "unsupported format)
Hello Noah, the Reduction Ratio seems to be a problem.
Can you check your Configuration in the engineer.
Maybe 0,5 is selected? (you can also send me the Wireshark snipped so i can see which parameters are beeing written.) Select something higher for a try.
I did not try the module myself but a colleague used it successfully I think.
Unfortunatly he is currently on holiday.
I will try it out myself when I get the chance. kind regards,
I have solved the issue. I adjusted the ReductionRatio for the GW from 8 to 32 (This was an arbitrary change). There is a connection now, however, it updates at a slow rate. This is okay for my application though.