Incorrect Behavior of Coils Connected to Function Blocks

PLCnext team:
I would like to post photos / videos of the behavior of coils that are connected to Function Blocks; PLCnext does not behave as logical thought (or “relay logic” would dictate). I have screen shots of Allen-Bradley controllers, CoDeSys controllers, and Omron controllers – they all behave the same (but different than the PLCnext controller).
However…I STILL cannot post photos to this forum.
Please contact me via the email address I used to register for this forum and I can supply the documentation of this behavior.
Thank you,
SFW

Steve,
A function block with the EN/ENO parameters will hold the previous state when the input (EN) is turned off. The ENO will not go LOW even if the input (EN) is disabled.

Thank you,
Dalton Gilchrist