It is possible to do a Modbus TCP Communication with other PLC?

Hi,
I’m currently working with the EPC 1502 and I’m triying to configurate a Modbus TCP communication with an other PLC.
In the User Manual of PLCnext shows that only AXL devices can use ModbusTCP modules.
Is that true? I can communicate via Ethernet using other PLCnext module?
Thank you in advance!
Kind regards,
Guillermo Zarate

Hello,
the EPC can be programmed like a PLC with PLCnext Engineer. There is a Modbus TCP library available from the PLCnext store that you can use for Modbus communication.