Local bus error
I’m testing out a bit with a PLCNext engineer project. When I upload the project, there are no errors/warnings in plc engineer, but the D led of the axcf2152 is flashing, so I found it’s a local bus error.. I am just working with the starterkit and I just want to switch some leds. Which device is the led/switch module on the right of the starterkit? I added the AXLF DI8/1 DO8/1 1H, which is coupled. The outputs of the program are coupled to the outputs 00-07 of that module. Are these visable on the leds? I see the leds switching in the PLC-plant, but not on the module. Is the local bus error causing this? Is it possible to fix this? The leds on the AXLF DI8/1 DO8/1 1H are reacting to the switches of the right module, so I assume the project is not uploaded properly… Arne
After I turned off the whole controller and turned it on again, I can’t connect anymore in PLCnext engineer. Also winscp is showing: Network error: connection to “ip” refused. So it is the right IP, otherwise it was showing connection timed out…
Hi Arne, In answer to your first question - the D LED indicates that the hardware configuration is incorrect in the PLCnext Engineer project. As for the second problem - I understand that you cannot connect to the PLC using PLCnext Engineer or WinSCP.
                                               * What LEDs are on/off/flashing (with colours) on the PLC?
                                               * Can you please try using PutTTY to connect to the PLC?
If you are able to connect with PuTTY, then please send us the contents of the file /opt/plcnext/logs/Output.log on the PLC, which should help us diagnose the problem with the PLCnext Engineer connection. Martin.
I can’t connect to putty.. Also refused. I will reset the controller. Run (green) and BF-C, BF-D (flashing red 1hz) and D (flashing red 0,5hz) are on. I am not using any profinet devices (I read thats why BF-C and BF-D leds are flashing red). I see it’s not possible to add a project in the attachment. Arne
Hi Arne, those LEDs all look fine - it looks like the project is running OK. Is there a chance that you somehow changed the IP address in the PLC? In PLCnext Engineer, please try using the “Scan Network” function (round button on the top-left of the "Online Devices tab in the Project window). This will scan the network and should discover the PLC and show its IP address. Martin.
Some answers to your original questions:
                                               * The flashing D LED indicates that there is a mis-match between the configured and the actual hardware configuration. It is OK to run the PLC like this, but you won't be able to access any missing I/O modules from the PLCnext Engineer program. To eliminate this error, please check that you have also included the Analog I/O module in your hardware configuration.
                                               * On the starter kit, the digital outputs are not wired to anything. You will see the orange LED on the Axioline I/O module light up when the corresponding output channel is turned on, but that's it. If you see these LEDs switching, then your program is working OK. Of course you are free to wire these digital outputs to any device that takes a 24 VDC input signal.
                                               * The LEDs on the little switch module simply indicate the status of the corresponding toggle switch.
Martin.