I connected to a new 2152 PLC, but something strange happened, and I see an orange shield whenever I connect to the PLC (at one point it was the normal blue one). I am still able to download new programs and debug. Is this related to certificates? How to solve this? Thanks
Hi Alex. This symbol is most commonly seen when User Authentication is disabled from the Web-Based Management page, although strangely the PLCnext Engineer help system does not seem to mention this at all. If you suspect it is a certificate issue, what do you see when you hover over the orange shield?
Hi Martin, This is what I see:
Is user authentication enabled in WBM? Or is it disabled?
It is disabled
I enabled it and now I get the Blue Shield. Thank you!