Dear Sir, Need some detail about OPC UA server for AXC F 2152.
1. How many monitored item or elements we can register per subscription in OPC UA server. 2. 2\. How many subscription we can use per CPURegards Chetan
Hi Chetan, sorry for the late response, but due to the current “Corona Situation” some topics needs a bit longer… However, I’ve spoke with the dev and we do not have a certain limit of max. used subscription, means it depends on the overall load of the PLC. Important to know is the fact that all subscriptions are configured in the default mode to work task synchronous (real-time mode).
This is great if you need synchronous data, but could lead by using a high amount of subscriptions also to a task watchdog. Since FW 2020.0 LTS it is also possible to configure the subscriptions as “direct read”. In that case you are not longer task synchronous,
but a lot faster and longer depending to the cycle time of the task. You can change the key as follows (documentation will be updated later): /opt/plcnext/projects/PCWE/Services/OpcUA Add the following lines (delete the * before → add those that the editor takes the xml ?)<*SubscriptionSetting>
<*SubscriptionKind> DirectRead
<*/SubscriptionSetting>Take care Frank
Thank you Frank. I will try to update after lockdown. Also number of subscription per CPU , is it like no of Sockets CPU can handle independently , as we can Change 4840 port . Regards Chetan