Hi,
I am using strings to store engineering unit information for values, but special characters are not showing correctly in the HMI.
Examples are:


* °C
* µ
The below screenshot shows the symbol rendered for degree centigrade.
Is this a limitation in the IEC-standard or in PLCnext Engineer’s parsing of character sets between PLC and HMI ?
Hello!
You should use WSTRING datatype for this proposes.
Best regards.
Hello!</p>You should use WSTRING datatype for this proposes.</p>Best regards.</p>
Great.
Learned something new ![]()
From the above picture, I present the value and the unit in two different Text-symbols.
The value is a real, the value is a WSTRING.
Is it possible to combine these two into one Text-symbol? I have tried concat, but that only works for strings.
TO_WSTRING (with the required formatting) plus CONCAT should do it, I think.