Hello, in our example Project we are using the PLCNext OPC UA Server for interfacing to the IT infrastructure (in the test setup to UA Expert and a Node-Red OPC client). The PLCNext is running Firmware 1.0.0.250 Read and write is working fine from and to the UA Server. Trying to subscribe to the same node either via UA Expert or a Node-Red OPC UA Client isn’t working. In UA expert the value is initially retrieved, but afterwards never get updated values. Is this a known issue and is a workaround available? Best regards Andreas
Hello, I could not reproduce the behavior you described.
With multiple subscriptions to the exact same node from different sessions (same or different Encryption) It seems to get stuck however(UaExpert V1.4.4) if I create multiple Session with the same name. (UaExpert tends to do that Every time I add the AXC F 2152 as Server a session with the identical name is creatend and UAExpert almost gets stuck. in that case simply use Advanced settings to change the sessionname manually and you should be good to go.) But in any case I always got unlimited updated values.
Wich PC Worx Version are you using and how many Subscriptions do you have running from each session when it gets fauly? (I tried like 10 Subscriptions to the same node from different/or the same Sessions simulatineously.)
Wich Datatypes are you subscribing?
Hello, I am now able to repeat the behaviour in UA Expert. All values get updated in UAExpert in case they are coming from the same Folder. As soon as you add nodes from a different Folder all nodes in the Data Access Viewer are not getting updated anymore. See the attached gif for the node main_colorSensorMinValue. In DataAccessView it still Shows the old value 7000, while in Attributes Viewer it shows the newly updated value 5000. In Node-Red I changed to the latest release of node-red-contrib-iiot-opcua and it shows the same behaviour like in UA Expert. If all nodes are coming from the same folder the subscriptions are working fine. In case I add to the same listener nodes from a different folder, the subscriptions doesn’t get updated anymore.
Hello, I tried reproducing this with FW 1.0.1.8 and it was working fine for me. The Attribute is only once refreshed when changing focus in the address Space. The Data Access View is refreshed continuously. 