ProfineDevice don't connect

Hello all,
i have the serious problem with attaching ProfiNet device. In Online devices i found the IL-PN-BK device, insert in project (i set the right version of coupler and DO card). After upload to PLCnext i get BF-C error . In WBM is shown error 0x0023, and the coupler is in error no PN communication, „A profinet connection can be established to the device.“
When i change PLC to Simatic S7, the communication with this device work smoothly.
PLC AXC F 2152
Firmware Version 2021.9.0 (21.9.0.40)
Hardware Version 02
FPGA Version 1.1.78
PLCE 2022.0.1

Hello, hwsoft!
I met with same trouble too, a couple of times.
I don’t know what is under the hood, but always solve this case with downgrade of plc fw to 2021.6 or 2021.0.5 LST, and then up to 2021.9.
What i mean. You download your project to plc, and then use WinSCP and Putty to provide firmware downgrade\upgrade on the plc side.

Best regards.

The following are the results from a colleague who tested this configuration:
I created a test environment with following parameters:

AXC F 2152 FW 2022.0.3PLCnext Engineer 2022.0.1IL PN BK FW 1.00IB IL 24 DO 8

I cannot reproduce the failure which was explained.inline-173800837.pngSteps in PLCnext Engineer:Open PnE 2022.0Open the view "Profinet"Select "Online Devices​inline-1606064054.pngCheck if the PN-Device name is taken by the device (Netnames)Write and start project on the PLC​