I am trying to communicate in profinet between 2 AXC F 2152 PLC’s. i am able to communicate in profinet. But, the Profinet input data is not updating the connected field Input_data instead it is updating in PND_S1_INPUTS. Please refer the below screenshots.
PNImage5.pngPNImage4.pngPNImage3.pngPNImage2.pngPNDEvice.pngpn-comm.pngPNimage1.pngHello,
one of the PLCs must be integrated as Profinet device into the PLCnext Engineer project of the other PLC.
On the “device PLC” you can use the system variables PND_S1_INPUTS and PND_S1_OUTPUTS to exchange data with the “controller PLC”.
On the “controller PLC” you can use the process data of the “device PLC” DI4096 and DQ4096