Dear Community members, I tried to configure IOL MA8 PN DI8 (IO-Link master / 1072838) for AXC F 2152 on PLCnext Engineer 2019.3 GSDML file : GSDML-V2.34-Phoenix-IO-Link-20181102.xml Unfortunately, I can see warning on it. “Warning: Type does not match! project: ‘IOL MA8 PN DI8’ online: ‘IO-Link Master’.” PCNE001.PNG Is this any mistake?, how to clear this worning? Or, ignore it ?
Hi Ttakenaka, looks strange. I’ve unfortunately now none of those new IOL master on my desk, but I’ll try to get one and will come back to you later. Take care
Hi Ttakenaka, sorry for waiting that long, but finaly I’ve got one of those on my desk. There is a mistake in GSDML relating the name string. In the GSDML is “IOL MA8 PN DI8” defined, but on the device just “IO-Link Master”.
Some PN configurators does accept this, but PLCnext Engineer is there quite strict. However, we will deliver a new GSDML, but in the meantime you can easily fix it by changing the GSDML as follows: From
TextId="TOK_Mod_Name_IOLMA8PNDI8" Value="IOL MA8 PN DI8"To
TextId="TOK_Mod_Name_IOLMA8PNDI8" Value="IO-Link Master"Just save the GSDML, remove the existing one from your project and reinsert the modified one again. Good success! Frank
Hello Flank-san, I just try it, ignore that warning now at my system. Danke schÖn Toshiki Takenaka