Reading data from M-Bus meter. (Meterbus, Mbus, Meter-Bus)
I’m trying to read data from meter with the AXL F MA MBUS 1H module on a M-BUS but it wont work. I have attached the module to a AXC F 1152 controller and downloaded the M-BUS library from PLCnext Store and added it to PLCnext Engeneer 2020.6 Information about the AMS meter: Adress: 4 Update time from meter 2,5 second for kW. I have attached the table for the comunication here. I need kW, L1-Amps, L2-Amps, L3-Amps and kWh I cant find any examplecode that works. Can someone make a simple program for reading data from the meter. Please use NOLD code (Ledder)?
Hello pudderjagar, in the help file of the function module SE_MBU_MbusClient you’ll find an application example for LD which should also work for NOLD. A ready-made example cannot be provided by us at the moment. Best regards Marcel
Hi This is great. But I have discover a problem. The Kaifa AMS energymeter is set up as M-BUS MASTER!!! Not slave as usually. Does it make problems or is it possible to change the AXL F MA MBUS 1H module to act like a slave?
The Axioline MBUS master module cannot act as an MBUS slave (sorry).