Hello engineers on commnunity ! So i have the problem when i approach with RTC , which is not true with the current time , i tried reset the" Factory reset " , it’s still not working, how can i fix it ?
Regards.

Are you asking how to set the RTC on the controller?
If you are online with your controller, you can go to the controller name in the project tree (in your screen shot, it is called AXC F 2152 located right below the word "Project"). Double click this.
On the "Cockpit" page, there are a number of icons across the top.
In the middle of the icons, there is a clock with a "right" arrow.
If you click this, it will write the time to the controller.
PS: I was going to paste a screen shot to show you, but I'm still looking at how to paste an image in this response.