SBT communication with LPSDO8/3

Hi Team, I’ve been trying to connect our AXC F 1152 with the LPSDO8/3. In SAFECON I have a solo LPSDO configured with Island number 1. In PLCNext Engineer I followed the instruction video’s that come with the SBT package. I have added a SBT_V3_Operate_2 block and all blocks stated in the video. The Operate block include ‚islandNo‘ 1. On the hardware I have set the DIP switches according to the image on the SAFECON (010000100000 Left to right). Yet when I try to execute the Operate block it response with wDiagCode 16#C001 and wAddDiagCode 16#0004 which says „Wrong or invalid island number or no satellite configured for the LPSDO“. What can I check to get it working now? Is it possible to have a solo LPSDO8/3? Other units are on backorder right now. Thanks in advance. Carel

Hi Carel, Unfortunately it is not possible to start-up a LPSDO8/3 without a safety input module. Please add a AXL SSDI in your SAFECONF configuration and download it again to the LPSDO8/3. Then you will get a error message regarding a missing module but the safety program should run. Best regards! Volker