Simulink conecction

Captura de pantalla 2022-05-26 111115.pngCaptura de pantalla 2022-05-26 111208.png

Good morning, I get this error when executing the program in Simulink - PLCnext in external mode, is there a target apart from those that are downloaded from the website of the PLC itself (in my case the EPC1522)?
Do I need some type of target related to PLCnext for the Hardware Board in simulink ?

It looks like you’re trying to connect directly to the PLC from Simulink … is that right?
If so, then I don’t think that will work. The simulink model must be compiled into a PLCnext Engineer library, which must then be added to a PLCnext Engineer project, which is the software that must be used to connect to the PLC. You can then (optionally) view the „live“ Simulink model in PLCnext Engineer, by ordering a license for the Add-in viewer for Simulink:
image.pngThis should work if you follow the steps in the User Manual. If not, please let us know exactly which step in the User Manual is not working for you.

How can I request that license for the plugin viewer for Simulink?

Please get in touch with the Phoenix Contact sales office that services your country, and they will explain how you can order that license.

Thanks a lot!