TryGetTaskInfoByProgramName Warning

I don’t understand this warning in my log: 03.01.18 15:15:01.793 Arp.Plc.Gds.Internal.Subscription.SubscriptionBase INFO - Subscription 16 subscribed.

03.01.18 15:15:01.846 Arp.Plc.Meta.DataDictionary WARN - TryGetTaskInfoByProgramName: Could not find task info for program: Arp.Io.FbIo.AxlC/0
03.01.18 15:15:01.850 Arp.Plc.Meta.DataDictionary WARN - TryGetTaskInfoByProgramName: Could not find task info for program: Arp.Io.FbIo.AxlC/0
03.01.18 15:15:01.852 Arp.Plc.Meta.DataDictionary WARN - TryGetTaskInfoByProgramName: Could not find task info for program: Arp.Io.FbIo.AxlC/0
03.01.18 15:15:01.855 Arp.Plc.Meta.DataDictionary WARN - TryGetTaskInfoByProgramName: Could not find task info for program: Arp.Io.FbIo.AxlC/0
03.01.18 15:15:01.858 Arp.Plc.Meta.DataDictionary WARN - TryGetTaskInfoByProgramName: Could not find task info for program: Arp.Io.FbIo.AxlC/0
03.01.18 15:15:01.861 Arp.Plc.Meta.DataDictionary WARN - TryGetTaskInfoByProgramName: Could not find task info for program: Arp.Io.FbIo.AxlC/0
03.01.18 15:15:01.870 Arp.Plc.Meta.DataDictionary WARN - TryGetTaskInfoByProgramName: Could not find task info for program: Arp.Io.FbIo.AxlC/0
03.01.18 15:15:01.873 Arp.Plc.Meta.DataDictionary WARN - TryGetTaskInfoByProgramName: Could not find task info for program: Arp.Io.FbIo.AxlC/0
03.01.18 15:15:01.875 Arp.Plc.Meta.DataDictionary WARN - TryGetTaskInfoByProgramName: Could not find task info for program: Arp.Io.FbIo.AxlC/0
03.01.18 15:15:01.889 Arp.Plc.Gds.Internal.Subscription.SubscriptionBase INFO - Subscription 17 subscribed.
03.01.18 15:15:08.818 Arp.Plc.Gds.Internal.Subscription.SubscriptionBase INFO - Subscription 16 unsubscribed
03.01.18 15:15:08.829 Arp.Plc.Gds.Internal.Subscription.SubscriptionBase INFO - Subscription 17 unsubscribed
03.01.18 15:16:54.175 Arp.Plc.Meta.DataDictionary WARN - TryGetTaskInfoByProgramName: Could not find task info for program: Arp.Io.FbIo.AxlC/0
03.01.18 15:16:54.178 Arp.Plc.Meta.DataDictionary WARN - TryGetTaskInfoByProgramName: Could not find task info for program: Arp.Io.FbIo.AxlC/0

Hello Marcel, I guess you did not connect the mentioned Variable “Arp.Io.FbIo.AxlC/0” via the GDS.

Therefore no GDS Memory is reserved for this Variable.
PC Worx Engineer trys to subscribe(while debugging) the variable “Arp.Io.FbIo.AxlC/0” from your GDS → but it does not exist so it fails.

The “Program” in this case should be the AxioBusSheduler.
It should not ouccur anymore if you connect the variables via GDS.

Where can I find this var? I didn’t find “AxlC” in eclipse or PC Worx.

-AxlC/0 should be the first module of your local bus. currently the Instance address is not shown at the variable datasheet anymore but you can see it if you add the variable to the watch Window.