Hi, I have a problem sending an UDP telegram, see enclosed code. When the project started, a UDP message is sent only once, a sniffer shows the message with the correct data. After this first transmission, UDP_SEND_21.DONE remains false. As this is my first project, I will probably overlooking something… Thanks in advance for any reply, Cock van der Meer 2152 controller, version 2021.6.0 PLCnext engineer 2021.6
Hi, it looks like the UDP_SEND_2 FB instance is only ever called with REQ := TRUE. According to the documentation: [quote]A rising edge at the request REQ input triggers the transmission of the data applied to the DATA input.[/quote]So (unless I am mistaken) there will only ever be one rising edge, the first time this FB is called. I see that the FB instance is being called conditionally, inside an IF … THEN … ENDIF statement. I usually recommend to call all FB instances unconditionally in a program, and then use the conditional statements to set the FB instance parameters - like the REQ parameter on the UDP_SEND_2 FB instance. That might be a quick-fix for the problem you’re seeing.
Hi Martin, Thanks for your response. I already did removed the IF statements and also set REQ to low after sending etc. See the out-commented lines. This did not gave any results. When a cyclic task runs it first cycle, does the task then behaves different form consecutive cycles? As I’m a newbie to PLCnext, what would be the correct approach if I want to send every xx milliseconds an UDP message to the network? (Application is continuously acquiring 6 SSI encoders, do some math on the measurements and send an array of 7 INT32’s to the network in an UDP telegram.)
[quote]I already did removed the IF statements and also set REQ to low after sending etc. See the out-commented lines.[/quote]If you are referring to the screen-shot in the original post - even with the commented lines, the function block instance is still called inside two nested IF blocks. [quote]When a cyclic task runs it first cycle, does the task then behaves different form consecutive cycles?[/quote]No, but at the start of the first cycle all function block instances will have default values for all input parameters, e.g. REQ = FALSE on all UDP_SEND_2 FB instances. So if your code sets REQ := TRUE on the first cycle, this is recognised as a rising edge on this input parameter. [quote]what would be the correct approach if I want to send every xx milliseconds an UDP message to the network?[/quote]The approach you’re taking seems to be a reasonable solution. The main thing I’d do is move the call to the UDP_SEND_2 FB instance out of the IF blocks, and only set the REQ input for one cycle, at the frequency that you want to send the message. It looks like you’re trying to send a message every time the Counter1 reaches 20, so you could do something like: Counter1 := Counter1 + 1; IF Counter1 = 20 THEN SendNow := TRUE; Counter1 := 0; ELSE SendNow := FALSE; END_IF; UDP_SEND_21 (REQ := SendNow; ...) … where SendNow is a local variable of type BOOL. You might also have to add some checks that the previous message has finished sending - e.g. the BUSY output from the SEND FB could be checked in the IF conditions.
Hi Martin, Applying your suggestion to my code and it works! It looks to me that you have to ‚Reset‘ the UDP_SEND_2 FB with a function call rather then setting property .REQ to False? Or is there some compiler or runtime magic when a FB is handled within a IF/THEN? Still a lot to learn for me. Thank you very much for your support!
[quote]It looks to me that you have to ‚Reset‘ the UDP_SEND_2 FB with a function call rather then setting property .REQ to False?[/quote]I think you might be misunderstanding the way that function block instances work in IEC 61131 applications. A single call to the FB instance doesn’t spin off a separate thread to do the work - the FB must be called „continuously“ so it can complete its work, often over multiple cycles. This isn’t something that’s specific to PLCnext Engineer - we just follow the IEC 61131 standard. Our friends over at RealPars have some good training material on general PLC topics like this - it’s worth checking for something that might cover this topic. Even if it’s on a different PLC, the same concepts will apply.
[quote]the FB must be called „continuously“ so it can complete its work, often over multiple cycles. This isn’t something that’s specific to PLCnext Engineer - we just follow the IEC 61131 standard.[/quote] Thanks, this explains a lot!
Digging up an old thread, I use this UDP_SEND_2 function block. If I want to send a packet every single cycle, is this a way to do this? My understanding is it is safe because REQ will be ignroed if the handler is busy…
UDP_SEND_TASK(REQ := FALSE, HANDLE := udp_socket_handle, DEST_IP := '192.168.10.255', DEST_PORT := 61928, DATA_CNT := SIZEOF(status_pkt), DATA := status_pkt); UDP_SEND_TASK(REQ := TRUE, HANDLE := udp_socket_handle, DEST_IP := '192.168.10.255', DEST_PORT := 61928, DATA_CNT := SIZEOF(status_pkt), DATA := status_pkt);
Hi elidonner,
I don’t think that would work because as Martin explained in this thread:
Quote:‚the FB must be called „continuously“ so it can complete its work, often over multiple cycles‘
So if the FB may take more than one cycle you can’t send a paket each cycle.
If you want the FB to send a package asap you could try to change your code to something like:
UDP_SEND_TASK(REQ := NOT(UDP_SEND_TASK.BUSY),
I haven’t tried it myself but this should trigger the FB in the next cycle after all data has been sent.BR
DivisionByZero
Hi ,
I ran this and it seems to work just fine. The UDP_SEND_TASK will just ignore the send request if UDP_SEND_TASK is BUSY.