Upgrade project to 2019.6

HI, I have trouble upgrading project from plcnext engineer 2019.3 to 2019.6

After changing RFC4072s controller from 2019.0 to 2019.6 global variable in safety plc is not recognized as used in function block and the same global variable is showing read before write in another function block.
I have tested to create new variables and still the same issue.
The global variable is set in safety main work sheet with number [4] and the variable is read in a function block placed in number [5] work sheet. The project is the same as before upgrading. Have I missed something? Best regards Stefan

Hi Stefan! I don’t know the cause of the problem, but have you seen this statement under “3.3 Known limitations and errors” in the change notes for firmware 2019.6

“SafetyBridge Technology
Reliable operation in conjunction with SafetyBridge
Technology is not ensured.
If you want to use SafetyBridge Technology, use the
controller with firmware version 2019.3.”

It might be related.
(That particular sentence made me not upgrade to firmware 2019.6)

Hi Tom, Thanks for the reply. I read the release notes but nothing there indicates the problem I have. /Stefan

I think I found the problem but I don’t know how to solve it. When I change the PLC-version it creates a second Safety task and the projects safety task is never executed. If I don’t change the PLC-version I have another fault “Error”,“”,“Internal Error : An item with the same key has already been added.” Is it possible to change safety task? can’t find anything in help. /Stefan

Hello Stefan,

sorry for the late response.
how exactly did you change the PLC Version you replaced the PLC right
Having two Safety Tasks is invalid. There must be something going wrong.
Unfortunatly we can not reproduce the behavior here.
So it might be related to something in your Project.
Can you supply your project or a backup for some test? https://phoenixcontact.sharefile.eu/r-r4e642c7badd441a8[

kind regards,
Oliver

](ShareFile)

Hi Oliver, Thanks for the reply. I first changed the library to the RFC from 2019.6 installation and then copied the controller from that library (Network/RFC/Devices/Controller/). Then I right clicked on the RFC in the left panel and used replace function. I hope that is the correct way. I have sent the project to Phoenix Sweden and I think he sent it forward to Phoenix Germany hopefully you can get it from there. There are no errors in the project in 2019.3. Best regards Stefan