I have a problem with retain value in FW 2025.0.3 on RFC4072s
If I reboot the PLC the retain value is kept but it is lost at power off/on.
Has anyone else seen this problem?
Br Stefan
Hi Stefan, I struggled with the same issue a while ago on a different controller. The answer was fully understanding the documentation and noting that „cold starts“ reinitialize all variables: https://www.plcnext-community.net/infocenter/extended_retain_handling/
„“"
Furthermore, IEC 61131 defines three start modes:
Cold Restart
- initializes all variables
- Warm Restart initializes only variables which are not indicated as “RETAIN”
- Hot Restart initializes no variables
„“"
In short, retention is ignored during a cold start, and a power cycle counts as a cold start. If you really need retention, you’ll have to use persistent storage on the underlying file system or SD card (if your controller supports this).
Hi,
Thanks for reply.
It would be really bad if power off/on is considered as a cold restart. The behavior is new, it was not like that in 2022 LTS version.
I hope Phoenix will come with a solution or an answer on why it happens.
Br Stefan