Skip to content

2020 Hotfix 1?

Hi

 

What is updated in Hotfix 1?
I cant fint it in the CHANGE NOTES on the site

 

-Emil

Comments

  • Hi Emil,

    I will check what is included with PLCnext Engineer v 2020.0 Hotfix 1, and let you know.

    ~ Martin.

  • Hello Emil,

    I had a CPU with the third problem.

    3 Changes in firmware version
    2020.0.1 LTS
    3.1 Error corrections
    The following problems have been fixed:
    – A problem that led to cyclical connection terminations of
    the PROFINET application relationships (AR). This
    behavior occurred depending on the cycle times of the
    ESM tasks.
    – A problem that caused an incorrect recovery of the
    retain data after a reboot of the controller. This behavior
    only occurred if program instances in the PLC project
    were moved to another ESM task.
    – A problem that caused the controller to stop booting
    after resetting the controller to factory default type 2
    (factory default). In this state the BOOT LED flashes red
    (2 Hz). The LED D is permanently yellow.
    – A problem that was possible in conjunction with
    OPC UA. Scalar data types could be written with the
    wrong data type. This could lead to incorrect data in the
    IEC project when overwriting with larger data types. The
    error code “StatusCodes.BadTypeMismatch” would be
    expected here.

    Grtz,

    Joker

  • Expect to see the change notes for PLCnext Engineer 2020.0.1 on the website some time next week.

    Sorry for the delay.

    ~ Martin.

  • Just in time  :)

    The release notes for PLCnext Engineer 2020.0.1 are now available for download from our website.

    Also attached here.

    ~ Martin.