Hi Guys,
I started last week playing with the AXC F 2152 controller and an AXL F BK ETH buscoupler (with 1 DI and 1 DO connected). At the moment I've got the communication up and running between the two and I can read the DI's. Now I thought I was ready to control the DO's but that was a bit of a failure.
I used the example code which is included in the Modbus_TCP_6 library to get the DI's up and running with FC4_3. For the DO's I think I must use FC16_3 I programmed it and tried some things but I cant get it to work. I got an error with wDioCode = '16#C060' and xAddDiagCode = '16#0004' ("Slave device busy").
My code:
The code in block 'Aansturen_MB_NDB2':
TON1(IN := xDelayStart, PT := tDelayTime, Q => xDelayReady, ET => tDelayE);
CASE iState OF
0: (* Wait for command *)
IF xStart = TRUE THEN
iState := 10;
END_IF;
10: (* Init *)
xWrite_NBD_Ready := FALSE;
xWrite_NBD_Busy := TRUE;
(* Client *)
udtClient.xActivate := FALSE;
udtClient.xAutoAck := FALSE;
udtClient.strServer_IP := '192.168.0.12';
udtClient.iPort := 502;
udtClient.xUDP_Mode := FALSE;
udtClient.tTimeout := TIME#10s;
(* FC16 function block *)
udtMB_TCP_FC16.xActivate := FALSE;
udtMB_TCP_FC16.iMT_ID := 1;
iState := 100;
100: (* Start *)
udtClient.xActivate := TRUE;
IF (udtClient.xActive = TRUE) THEN
iState := 1000;
END_IF;
1000:
udtMB_TCP_FC16.xActivate := TRUE;
udtMB_TCP_FC16.uiQuantityOfRegisters := UINT#1;
udtMB_TCP_FC16.wStartRegister := WORD#9001;
IF (udtMB_TCP_FC16.xActive = TRUE) THEN
iState := 2000;
END_IF;
2000:
IF udtMB_TCP_FC16.xError = FALSE THEN
udtMB_TCP_FC16.arrRegisterValue[1] := wNBD_DO2;
xDelayStart := TRUE;
IF xDelayReady = TRUE THEN // AND
xDelayStart := FALSE;
iState := 3000;
END_IF
END_IF
3000:
udtClient.xActivate := FALSE;
udtMB_TCP_FC16.xActivate := FALSE;
IF (
udtMB_TCP_FC16.xActive = FALSE
AND udtClient.xActive = FALSE
) THEN
IF xStart = FALSE THEN
iState := 0;
xWrite_NBD_Ready := TRUE;
xWrite_NBD_Busy := FALSE;
END_IF;
END_IF;
END_CASE;
// Is there perhaps a code viewer in this forum? I couldn't find it.//
The variable 'wNBD_DO2' is a 16 bit word which contains the values to control the outputs.
Thanks for your help! If you need more information, please ask.
Comments
Problem is solved. The buscoupler was still in the Plug and Play mode whereby activating the output is disabled.
Just another RTFM problem...