PLCNext Engineer 2020.0 (Build 4.0.250.0)
Controller: AXC F 2152, FW 2020.0 LTS (20.0.0.24752):

I've configured a static IP address: 10.2.3.213 / 255.255.255.0 / 10.2.3.1 but couldn't reach PROFICLOUD or any other external IP address. I logged on to the controller via ssh to check the /etc/network/interfaces file. The device address and mask were correct but the gateway address said 0.0.0.0 and had obviously not been transferred from PLCNext to the controller. After I corrected the interfaces file manually and restarted the system everything worked as expected. Funny thing?

Regards, Wolfram

 

Comments

  • Hi Wolfram,

    I create several new PLCnext Engineer v 2020.0 projects every week, all with a non-default Gateway address, and I have never had this problem, but that's not to say that it's not possible.

    Can you please confirm that this is reproducible behaviour, if so then I will pass this to the PLCnext Engineer team, and they will let you know what additional information they need from you to investigate further.

    ~ Martin.

  • Yes, it seems to be a reproducible behaviour.

    I just configured a new gateway address like this

    address 10.2.3.213

    subnetmask 255.255.255.0

    gateway 10.2.3.2

     

    and uploaded it to the controller.

    Logged on with SSH and using ip r I've got this:

    root@axcf2152:/opt/plcnext/# ip r
    default via 10.2.3.1 dev eth0
    10.2.3.0/24 dev eth0 scope link src 10.2.3.213
    root@axcf2152:/opt/plcnext/#

    The gateway address did not change from 10.2.3.1 to 10.2.3.2. Where am I wrong?

    Regards, Wolfram

  • Hi Wolfram,

    OK, I have reproduced what you are seeing, and this was my misunderstanding.

    Using PLCnext Engineer, it is only possible to change the IP parameters of the PLC using the Project -> Online Devices window:

     

     2020 03 10 13 10 58

     

    This is way I have been setting the Default Gateway in my projects, so I misunderstood the problem (sorry!).

    It is not currently possible to change the default gateway by downloading a new PLCnext Engineer project to the PLC. From PLCnext Engineer, this can only be done from the Online Devices window.

    ~ Martin.

     

  • Thank you Martin - I got it!

    I assumed new IP settings are transferred with an upload as it is the case with Siemens PLCs, for example.

  • Yeah, this isn't clear in PLCnext Engineer. Hopefully this will improve in a future version.

    ~ Martin.