How to collect data from Profibus master with PLCnext Technology

edited August 2020 in PLCnext Engineer

How to collect data from Profibus master with PLCnext Technology [ AXC 2152 ] ? In case to exchange the data between 3rd party controller.

Do Profibus slave valid in this platform ?

 

Comments

  • Hello,

    Yes, it is possible to set up a Profinet controller to use an AXC F 2152 as a Profinet device.

    You can download the GSDML file from the product page on our website: 

    http://phoenixcontact.com/product/2404267

    In the AXC F 2152, the following gobal variables are used for Profinet process data exchange with the Controller:

    • PND_S1_OUTPUTS: Data from device to controller (maximum 512 bytes).
    • PND_S1_INPUTS: Data from controller to device (maximum 512 bytes).

     Hope this helps.

    ~ Martin.

     