Warning occur when scan inovance Servo through Profinet in PLCnext Engineer

Hello Sir

When I import the inovance Servo GSDML ,and scan it ,it show that warning as following picture: Revison doesn't match . However, it can be import to TIA portal as normal. And I upload the GSDML document as attachment . Please check it.

warning.png

Thank you very much for your help!

Comments

  • Dear User,

    as you've mentioned is this just a warning, you can still import the device into your project.

    However, we've checked the GSDML and it includes the following key:

    <!- optional keyword: <SoftwareRelease Value="V4.3" />

    As the online device have obviously a newer FW version is the warning correct, but I agree it would be nice if the warning shows also the FW version in the GSDML.

    Hope that helps.

    Take care,

    Frank!

     