Connecting 1 OUTPORT to Many INPORTS

edited January 2021 in PLCnext Engineer

I want to work with several program's on  1 controller. 1 program is a kind of overal runtime handler which handles, for example, the reset handling.

I want to push the resetsignal, detected in the runtime handler to all other program;s.  Working with a global variable is not possible because the

scope from a variable can not reach beyond the runtime.

So i want to make the resetsignal an OUTPORT for the runtime program and INPORT for all other program's.. Is this possible? And how?

 

Thanks,

Marco van Os

GeoComfort

 

Comments

  • Hello,

    You can duplicate the OUT port using the context menu in the PLCnext Engineer "Port List":

    2021 01 29 10 54 38

     

    ... then you can connect the duplicated OUT port to another IN port.

    Hope this helps.

    ~ Martin.

     