It is possible use the AXC F IL ADAPT with PLCnext 1152 to read a IB IL PROFIBUS MA-PAC ?(2700630)
a customer bought this equipment to read profibus dp and send the information to a scada through plcnext 1152, but according to what i have found out, this configuration is NOT possible, so the solution should be plcnext 2152 + AXC F XT PB. but before giving him this info i would like to know if the configuration shown in the image to read the profibus equipment is indeed possible or not.
Comments
the IL PB MA is not released for PLCnext Engineer, so you've to use the proxy instead.
BR,
Frank
just a small additional hint.
Next to the old proxy we've an even better alternative with the new GW PN/DP 1E/1DB9 - 1108712.
BR,
Frank
greetings
Milton